There is no communication between the controller and the panel. OPC UA.
Hello!
I followed the steps:
1. Made the settings for OPC UA on the controller;
2. Created a new project in the VISU 2.54 environment;
3. Launched the VISU project in RUNTIME mode (clicked Start Project);
4. In RUNTIME mode, the project is running, there is communication with the controller;
5. Uploaded the project to the panel;
6. The panel is working;
7. There is no communication between the controller and the panel.
What is the problem?
Starter kit provided by Phoenix Contact:
- controller: AXC F 2152;
- panel: TP3120W / P.
I followed the steps:
1. Made the settings for OPC UA on the controller;
2. Created a new project in the VISU 2.54 environment;
3. Launched the VISU project in RUNTIME mode (clicked Start Project);
4. In RUNTIME mode, the project is running, there is communication with the controller;
5. Uploaded the project to the panel;
6. The panel is working;
7. There is no communication between the controller and the panel.
What is the problem?
Starter kit provided by Phoenix Contact:
- controller: AXC F 2152;
- panel: TP3120W / P.
Comments
... than save changes, send the project to the controller, and then restart the controller before testing again with Visu+.
.
This is not related to VISU+. The Plcnext Firmware was changed the OPC UA Namespaces Name Index. This is the reason that VISU+ is confused.
Please check that you are using the correct template in PLCnext Engineer.
You need to have 2021.0,x.
Then check also this document, which you can find on the Phoenix Contact Homepage
https://www.phoenixcontact.com/online/portal/us/?uri=pxc-oc-itemdetail:pid=2988544&library=usen&pcck=P-19-08-01&tab=1&selectedCategory=ALL
Article 2988544 --> Download Areas --> Application Node --> VISU+ OPC UA IMPORT Instructions on how to import OPC UA variables from PLCnext Engineer into Visu+ and Visu+ Express
--> ah_en_visu_opc_ua_import_109303_en_02.pdf
Please create for your test a complete new VISU+ 2.54 project with OPC UA client.
If this is not helping, then contact Support (OpMon Group). We will contact you fast as possible.
Thanks and good luck.
Alex L.
This is true:
... however, as discussed in another thread, an OPC UA server is allowed to change the namespace index. If an OPC UA Client like Visu+ does not handle this correctly, then there is nothing that can be done in the OPC UA server to fix this. Here is the relevant section of the article from Unified Automation that is referenced in that other discussion:
This issue - which might not even be related to the OPC UA namespace index - is currently being handled directly with Dmitry by the OpMon support group (ref: #220449).
.
And by the way. With Version 2.54 Visu+ can also work with changed Namespace Index
The best way is to ready the enclosed document.
We have a lot of customers with OPC UA and TP3000 and TP6000. I would expect, that we should get this running.
Best regards
Alex L.
In this case the problem appears to have been due to an old firmware version on the display panel.